    Rule 26-242 (2) states that dielectric liquid-*****d pad-mount distribution transformers shall be installed, "...at least 6m from any window, door, or ventilation inlet or outlet on a building."

    Does this distance include windows, doors etc. on the second floor of a building?

    If so, the notwithstanding clause 26-242 (4) allows for transformers to be installed within this distance provided that "...a wall or barrier with noncombustible surfaces or material [is] constructed between the transformer and that door, window...".

    Would this barrier have to be as high as the line-of-sight between the transformer and the second floor window or door? This would mean a pretty high barrier wall.

    Just wanted some clarification. Thanks.

  2. #2
    Inactive Member Tony Moscioni's Avatar
    Join Date
    June 4th, 2002
    Posts
    59
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Arrow

    This Rule applies only to dielectric liquid-*****d electrical equipment containing more than 46L in any one tank or a total of 137L in a group of tanks.

    The intent is to keep burning material away from areas of a building that are susceptible to spread fire in the event the transformer faults and ruptures.

    The 6m requirement IS measured "line-of-sight"

    Choices are to locate the equipment a suitable distance from combustible surfaces or openings, or installing fire-resisting barriers between the equipment and combustible surfaces or openings.

    An example of such a barrier would be a concrete or masonry wall built around three sides of a transformer mounted at the side of a building.


    The minimum distance of 6m to doors, windows and ventilation openings cannot be reduced without the use of a suitable fire resistant barrier, unless the transformer is single phase, 167 kVA or less, and has an integral current-limiting device.

    Tony Moscioni
    Electrical Inspector
    Electrical Safety Authority

  3. #3
    Inactive Member p-elec's Avatar
    Join Date
    June 14th, 2002
    Posts
    9
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Thanks for the help Tony.

    I'm assuming this line of sight would include, say a window within this length on the second floor. If so, would I have to build a wall to protect this line of sight? Meaning the wall could possibly be a storey or more high.

  4. #4
    Inactive Member twh's Avatar
    Join Date
    April 3rd, 2002
    Posts
    93
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    You could put a roof over it.